XW generator start question [RE-wrenches]
William Miller
wrmiller at charter.net
Fri Apr 25 11:14:19 EDT 2008
<x-flowed>
Dan/Jay:
This quirk may actually be a "feature." This might allow one to use the
Grid input as a second generator input. If the auto start circuitry is
independent of the Input 2 voltage sensing, one can connect a generator to
either or both AC inputs. Coincidentally, we are installing our first XW
this week and may need this option.
Next question: Can one install two GSMs????
William Miller
At 07:22 AM 4/25/2008, you wrote:
>Hi Dan,
>
>So they designed the GSM to use the 12v generator as the start signal
>and not the AC?
>What were they thinking?
>
>Thanks for the info on how to get around it.
>
>I've got a upgrade to get rid of some old SW's and thought it time to
>try an XW.
>
>thanks,
>jay
>
>peltz power
>On Apr 25, 2008, at 12:07 AM, Dan Rice wrote:
>
>>
>>Jay,
>>
>>Yes, the GSM is required to interface a generator to the XW, 2-wire
>>start or
>>otherwise. The GSM also requires a "generator running" signal in
>>order to
>>recognize a running generator and hold the 2-wire signal "on". The
>>GSM "run"
>>sensor circuit requires a 12 volt nominal (30 volts max) signal
>>from the
>>generator, and requires another 2 wires between the generator and
>>the GSM,
>>so for a "2-wire" start generator, actually 4 wires are required.
>>Xantrex
>>has heard the complaints about this loss of a true 2-wire start
>>feature on
>>the XW, and I understand that there's a software upgrade available
>>that will
>>allow the GSM to recognize when there's AC line voltage present at
>>the AC
>>input terminals of the inverter (AC 2 in, I assume). This should
>>eliminate
>>the need for the 12 volt "run" signal (and the extra 2 wires) from the
>>generator to the GSM. I haven't tried this upgrade myself. On the one
>>installation I've worked on, I ran the additional 2 wires, and
>>piggy-backed
>>off of one of the propane solenoids for the 12 volt "run" signal.
>>The GSM
>>works fine this way.
>>
>>I hope that helps.
>>
>>Dan Rice
>>Abundant Sun, LLC.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list