Big Offgrid System Request for Guidance [RE-wrenches]

Darryl Thayer daryl_solar at yahoo.com
Tue Apr 15 13:53:33 EDT 2008


HI Allen
First I assume you mean 300 kW peak load, not 300
kWh/day, 300 kWh/day could be handled by a 50 kW
inverter system.  BTW Outback can go bigger than 39kW
( know of at least one) I have not used a SMA island
system.

You are definitely getting good advice here.  Let me
just add a little.  Definitely conserve, Definitely
solar thermal.  Definitely due a load analysis.

For some guidance and basic sizing I like RETScreen
easy to use, and with a few work arounds, fast and
comprehensive.  Also Use Homer from NREL, I compared
predicted results and real real results found good
agreement. 

When doing electrical sizing use NEC Chapter 2 
Definitely use 2 gen-sets as they will require down
time for repair/maintenance.  

System type, I would say definitely 3 phase.  As a
rule, when the 5% volt drop makes the wire size larger
than ampacity go to a higher voltage.  This criteria
lets 480 3 phase up to about 1000 to 1500 feet. 
480/277 and 120/208 are very handy for building
wiring. There are some DGI inverters that go to 277.  

I have some ideas on battery technology, I will get
back to you on that. 
Good luck.
Darryl 




      ____________________________________________________________________________________
Be a better friend, newshound, and 
know-it-all with Yahoo! Mobile.  Try it now.  http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list