external chargers for Outback [RE-wrenches]
John Berdner
jberdner at sma-america.com
Fri Apr 4 13:42:32 EDT 2008
Bruce:
The Sunny Island 5048U has a 100 Amp continuous (120 Amps at low
battery voltage) charger in it.
At full power it is right around 90% efficient (as a charger or as an
inverter) and is Listed as a grid interactive inverter as well.
Best Regards,
John Berdner
Bruce Erickson wrote:
>
>
> Hello All,
>
> What have people used/been happy with when you need a large external
> charger for a grid-tied Outback system? We installed an IBE 24GPU70
> to generator charge 2 strings of 390 ah Trojans, and the thing seems
> to be very inefficient. Looking over the IBE sizing chart and
> comparing AC kw required for various continuous DC outputs, the
> efficiency seems to be in the 50-60% range, which is about what we
> observed in our system. Is there anything else out there that can
> deliver around 100 amps DC with reasonable efficiency and
reliability?
>
> Bruce Erickson
> Mendocino Solar Service
> PO Box 1252
> Mendocino, CA 95460
> 707-937-1701
--^----------------------------------------------------------------
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list