Mark:
I do not know the value or wattage of the resistor, but I'd hazard to guess
that this resistor is not going to trip the 175 amp inverter breaker, so,
yes, the breaker tripping or plain being opened manually un-bonds the
entire DC power system. This is precisely what gives me the creeps about
this whole concept.
Does anyone have the value of that component?
William Miller
At 10:13 PM 3/4/2008, you wrote:
>William et. Al.,
>
>In the diagram you post there is a resister across the 0.5A circuit breaker.
>Is it correct to say that the grounded DC conductor becomes "un-bonded" when
>the circuit breaker is open?
>
>Mark Frye
>Berkeley Solar Electric Systems
>271 Vistamont Dr
>Grass Valley CA 95945
>(530) 401-8024
>www.berkeleysolar.com
>
- - - -