The short Circuit was in the wireing between the
combiner and the Module, the actual short was between
the PV source circuit conductors.  The source of
current came from the inverter capasitor through the
fuse and negative return to the inverter.  I was in a
hurry and I should have climbed down and opened the DC
disconnect, but the old in a hurry get it done.
  
Darryl

--- Drake Chamberlin
<Drake.Chamberlin at redwoodalliance.org> wrote:

> 
> At 01:48 PM 2/27/2008, you wrote:
> >Are you sizing them Isc x 1.25 x1.25 ?
> >DT
> 
> I go with the manufacturer's recommendations, and
> put one per 
> string.  We have left them out when only one or two
> strings are 
> present on a direct grid tie.
> 
> Did your ground fault happen between the combiner
> and the first 
> module?  Would the scenario you experienced pose a
> danger to the modules?
> 
> Drake  
> 
> 
> - - - -
> Hosted by Home Power magazine
> 
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Moderator: michael.welch at homepower.com
>
> 
> 
> 
> 



      ____________________________________________________________________________________
Looking for last minute shopping deals?  
Find them fast with Yahoo! Search.  http://tools.search.yahoo.com/newsearch/category.php?category=shopping


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list