Evaluation of XW charge control [RE-wrenches]
Mark Edmunds
mark.edmunds at xantrex.com
Fri Feb 22 17:27:28 EST 2008
William, Wrenches -
I think our safety guys got a little carried away with that statement!
The XW charge controller is very robust and does not care in what order
the PV or battery lines are disconnected, no one in the lab ever puts
the units in standby before disconnecting power. I will see about
getting that wording changed in the manual.
Thanks for pointing this out,
Mark
Mark Edmunds
Xantrex Technology Inc.
-----Original Message-----
From: William Miller [mailto:wrmiller at charter.net]
Sent: Friday, February 22, 2008 1:17 PM
To: RE-wrenches at topica.com
Subject: Re: Evaluation of XW charge control [RE-wrenches]
Kirpal:
Thanks for your comments. This reminds me of a potential design defect
of the XW charge controller: The manual indicates that you must put the
unit in standby before disconnecting the unit or damage could result.
If indeed failure to activate standby mode on disconnect will damage the
unit, we consider this a design flaw. It is likely that untrained
customers will fail to navigate to the standby mode and instead just
activate the circuit breaker disconnect.
To prevent this, we are installing these controllers with two pole
breakers-- one pole for input and one for output. With this
configuration, the unit is entirely disconnected with one action,
hopefully preventing damage.
William Miller
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------