DC relay for 48V Power Vent [RE-wrenches]

Darryl Thayer daryl_solar at yahoo.com
Wed Feb 20 19:23:27 EST 2008


HI John
Once I used a solid state relay from Grainger, (for 48
volt fan) it was very small, an could switch from a 12
volt source to drive and capable of switching a 60v?
DC load of 3 amps?  if my memory is correct.  It is
still working I think.  also it was quite small if I
remember correctly.
Darryl


--- Windy Dankoff <windydankoff at mac.com> wrote:

> 
> John,
> 
> I agree with Christoper. I also add that mechanical
> switch contacts  
> rated at X Vac will have about the same arc
> potential (equivalent amp  
> rating) at 1/2X VDC. Therefore, a common 125VAC
> (contacts rating)  
> relay should work fine at the normal range of 48V
> system, especially  
> with oversized contacts.
> 
> To confirm this, look at relay specs. They usually
> do show DC voltage  
> ratings being about half that of their AC ratings.
> In that case, you  
> are really covered.
> 
> Windy
> 
> 
> - - - -
> Hosted by Home Power magazine
> 
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Moderator: michael.welch at homepower.com
>
> 
> 



      ____________________________________________________________________________________
Be a better friend, newshound, and 
know-it-all with Yahoo! Mobile.  Try it now.  http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list