Rinnai boiler controller [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Wed Feb 6 14:24:47 EST 2008
Adding the 50MFD motor run Capacitor to the inverter did not solve the
issue - theses Japanese heater systems seem extremely sensitive to power
quality.
The motor run cap does drastically improve the waveform of the SW - but
mostly when unloaded. The SW's waveform even at its best is still worse
than any of the HF PWM true sine waves - which are often 1% THD. These
heaters still seem to notice something...
The capacitor on the SW also increases the idle power consumption from
16 watts to about 35 or so - which is why we never built it in to the SW
at Trace. Be sure to put it on a switch if you add one to a system so
it can be connected only when required.
These motor run caps do not seem to make any difference on the FX
waveform other than a slight increase in idle power - a few watts if I
remember correctly.
On the lousy generator the motor run cap actually made it worse when I
looked at it with a O-scope!
Christopher
Christopher Freitas
Director of Research of Development
OutBack Power Systems, Inc.
cfreitas at outbackpower.com
Tel 360 435 6030
cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com
EMAIL CONFIDENTIALITY NOTICE:
The preceding message (including attachments) is covered by the Electronic Communication
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by
attorney-client or other privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you are hereby notified
that any retention, dissemination, distribution, or copying of this communication is
strictly prohibited. Please reply to the sender that you have received the message in
error, then delete it. Thank you.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list