Calculating string amperages [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Tue Feb 5 16:44:31 EST 2008
William,
I discern a difference between the term "Module Interconnection Conductors"
and "Photovoltaic Source Circuits" and "Photovoltaic Output Circuits".
Can it be that this citation is limited soley to the rating of conductors
connecting individual modules, not to the conductors associated with
"homerun" or "source/Output" circuits?
MPF
-----Original Message-----
From: William Miller [mailto:wrmiller at charter.net]
Sent: Tuesday, February 05, 2008 1:24 PM
To: RE-wrenches at topica.com
Subject: Calculating string amperages [RE-wrenches]
Jay:
Begin citation:
690.8 (D) Sizing of Module Interconnection Conductors. Where a single
overcurrent device is used to protect a set of two or more
parallel-connected module circuits, the ampacity of each of the module
interconnection conductors shall not be less than the sum of the rating of
the single fuse plus 125 percent of the short-circuit current from the other
parallel-connected modules.
End citation
Note above where it says "other."
What is not totally clear to me is that in an installation without a
combiner, i.e. connecting leads through a Square DU HU361 directly to the
inverter, are we meeting the "single overcurrent device" test of the above
section? It seems to me that the internal current limitation characteristic
of the modules makes the overcurrent protection inapplicable.
This code interpretation is explained pretty thoroughly and convincingly by
John Berdner in the SMA white paper. If you have lost the link, I have it
on our web site:
http://mpandc.com/resources/resources.html
This paper has been universally accepted in the industry and has passed
muster by the local building inspector code wonk guys. I used to submit a
copy with permit applications to forestall questions.
William Miller
At 08:05 AM 2/5/2008, you wrote:
>Hi William,
>
>Where is this subtraction of 1 string located in the code?
>
>thanks,
>
>jay
>peltz power
>On Feb 4, 2008, at 10:18 PM, William Miller wrote:
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list