Darryl - 

Paralleling two shunts with the FNDC does not require recalibration of the data as long as two of the FNDC's channels are connected to the shunts.  

Paralleling two shunts and connecting it to one channel of the FNDC will not work properly - the load current will appear to be half of the correct level.  This will result in the incorrect calculation of the battery start of charge as well.  

I did some checking and there are 1000 amp / 100 millivolt shunts available - AEE lists them in their catalog actually.  These are what is called a "C" size shunt - at least twice a big as the normal "B" size we included with the FW1000-DC and has the 1/2 inch bolts for connection.  The mounting holes are different as well.  

For really large systems - you can actually parallel three shunts together and have all three channels of the FNDC connected to it - this would give about 2000 amps of measurement (or so).  Each channel can measure up to 1000 amps - so it gives a total current of 3000 amps. 

Christopher 

Christopher Freitas
OutBack Power Systems, Inc. 

cfreitas at outbackpower.com 



EMAIL CONFIDENTIALITY NOTICE:
The preceding message (including attachments) is covered by the Electronic Communication 
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by
attorney-client or other privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you are hereby notified 
that any retention, dissemination, distribution, or copying of this communication is
strictly prohibited.  Please reply to the sender that you have received the message in 
error, then delete it. Thank you.


[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list