Evolution of the Quick connect [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Tue Jan 8 15:35:25 EST 2008
It get's a bit better since 690.33 E (1)(2)(E)
Interruption of Circuit.
Connectors shall be either (1) or (2):
(1) Be rated for interrupting current without hazard to the operator.
(2) Be a type that requires the use of a tool to open and marked "Do Not
Disconnect Under Load" or "Not for Current Interrupting.""
I don't think any of these vapor connectors are rated for full current rated
interrupt so they all have to have a tool....????
MPF
-----Original Message-----
From: Phil Undercuffler [mailto:p.undercuffler at conergy.us]
Sent: Tuesday, January 08, 2008 11:58 AM
To: RE-wrenches at topica.com
Subject: RE: Evolution of the Quick connect [RE-wrenches]
You say tomato, I say tomahto....
As a distributor, we've been struggling with this for some time now.
Multi-Contact makes two styles of connectors, neither of which (and I'm
not making this up) have been officially named. Their US website
describes them as Solarline 1
(http://www.multi-contact-usa.com/products/solarline/1) and Solarline 2
(http://www.multi-contact-usa.com/products/solarline/2).
However, the MC reps tell us that Solarline 1 & 2 aren't really their
names. They prefer to call them either First vs Second Generation, or
latching vs locking. To make things even more fun, on the other side of
the pond they go by MC3 and MC4, which is the diameter of their socket
and pin (3mm and 4mm respectively). Now doesn't that just provide
greater clarity? Or you can go by the catalog part numbers (PV-KBT3II
UR and PV-KST3II UR vs PV-KBT4/2.5 II and PV-KST4/2.5 II), which just
trips off the tongue.
If all this isn't entertaining enough, Tyco makes 5 different types of
plugs -- positive and a negative females, and positive, negative and
neutral males.
So why the change from First Generation/latching/Solarline 1/MC3 to the
new locking standard? 690.33(C) in the 2008 NEC states that connectors
that are readily accessible and that are used in circuits operating at
over 30 volts, nominal, maximum system voltage for dc circuits, or 30
volts for ac circuits, shall require a tool for opening. MC (and Tyco)
make optional sheaths which snap over their locking connectors, which
then require a tool to open the connector.
However, in an apparent code conflict that I haven't yet wrapped my head
around, 2008 690.31(A) states that readily accessible conductors >30
volts shall be installed in a raceway. (BTW, anyone have any good
suggestions how to make that work in this day of connectorized modules?)
If the connectors are accessible, then you need a tool to open the
connector. If the circuit conductors are accessible, then you need to
use raceway. But if you use raceway, then the connectors shouldn't be
accessible so you don't need to meet the tool requirement.
------------------------------------------------------------
Please note new phone extension!
Phil Undercuffler
Technical Services Manager
Conergy, Inc.
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Office | 505.473.3800 x4841
Fax | 505.473.3830
www.conergy.us
------------------------------------------------------------
-----Original Message-----
From: William Miller [mailto:wrmiller at charter.net]
Sent: Tuesday, January 08, 2008 9:20 AM
To: RE-wrenches at topica.com
Subject: Evolution of the Quick connect [RE-wrenches]
Friends:
I need to gear up for the quick connects on the Solar World modules. I
was
told by SW that the MC Generation 4 now used is the connector SW will
continue to use forever and that it meets the "audible click"
requirement
soon to be implemented by regulating agencies.
MC told me there is no such thing as a Gen 4 connector and that SW is
using
Gen 2.
At the Long Beach show, the Tyco rep told me that the next code revision
will mandate connectors that require a tool to disconnect the mating
pairs.
Have any of you researched these contentions? What are the rest of you
doing to prepare for future connectors?
William Miller
-- _________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600 Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list