[RE-wrenches] Inverter with two strings of different orientation
Peter Parrish
peter.parrish at calsolareng.com
Sun Dec 28 18:53:46 EST 2008
Bill,
I looked into this several years ago, and I was able to get some digitized
I-V data. I can't find that now (but I will). The data supports my claim.
Let's take the simplest case (constant cell temperature) and what was a
fairly popular PV module: Kyocera's KC200GT. Although it is a little tedious
to calculate the MPP, I found the following:
200 W/m^2 Vmp=25 V, Imp=1.514 A (37.9 W),
1,000 W/m^2, Vmp=27V, Imp=7.58A (205W)
For more realistic conditions (i.e. operating temperatures) the result will
be different and you could be right, but as far as constant cell temperature
concerned, there is a shift with irradiance.
By the way, the way you can see that there might be a real effect here is to
notice that Isc is almost perfectly linear from 200 W/cm^2 to 1000 W/cm^2,
whereas Voc is linear with irradiance only from 600 to 1000 W/cm^2.