[RE-wrenches] Outback VFX input voltage cycling

mick abraham mick at abrahamsolar.com
Sat Dec 27 16:23:34 EST 2008


Ron wrote: "The owner told me...that someone had wired a switch incorrectly
and when he turned it on the system "shut down". He then re-wired it and
everything appeared ok but I'm wondering if this fried a board."

Mick replies: I've seen several times with Outback and other brands (going as
far back as the Trace SW) where the inverter responds to an accidental short
circuit in the household wiring by shutting itself off quicker than a circuit
breaker can open. I'll bet that is what your customer experienced...possibly
due to a nicked hot wire in that new switch box shorting out to ground.

I suspect that (part of your customer's report) is completely unrelated to
your present problem scenario. If it was my headache I would beg, borrow,
or...rent a second generator to insert temporarily instead of the Honda 3800.
That's the most conclusive way to determine fault or no-fault on the generator.

Sometimes a genset will operate non-inverter loads OK and will exhibit normal
looking voltage etc. but there still could be transients or spikes which
render this input AC power unacceptable to the inverter/charger.

Thinking...there's not an auto-idle switch on that genset which may have
accidentally been set for auto, is there?

Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675



More information about the RE-Wrenches mailing list