Hi Mark,
No this issue I've had is that the mate just won't start the generator
with usual symptoms of system shut down.
But when I go to the mate and press start, generator starts right up.
All setpoints are correct. Replace the mate, and all is good, again
same setpoints.
So I can only surmise the problem is a mate issue that I've yet to
track down, but have a fix.
jay
peltz power
On Dec 15, 2008, at 8:38 AM, Mark Dickson wrote:
> Jay,
> Funny you should mention this. A customer just called today to say
> that his Mate has been failing to shut down his generator and they
> have been walking into a smelly room full of boiling batteries each
> time. Is this what you are referring to when the AGS’s are going bad?
> I recently replaced an older Mate with this one that has the updated
> firmware.
>