[RE-wrenches] utility EDS signage
Louis Woofenden
louis at woofenden.net
Wed Nov 19 13:38:40 EST 2008
Hi Phil,
Four out of the six of utilities that we deal with here in Arizona
require an external AC disconnect, and yes, we do install the plaque.
About half of the utilities explicitly require it, the other half don't.
I agree that is a confusing label, possibly leading service personnel to
believe a mostly non-existent danger exists. Then again, what do the
laws of physics and probabilities have to do with interconnection issues?
Best,
Louis Woofenden
The Solar Store
Tucson, AZ
> Our utilities require an external AC disconnect between the inverter and the
> point of interconnection, located next to the meter. In the past, we have
> marked this switch with the language in 690.17 (although no AHJ or utility
> has required it). Because we generally argue against the necessity of this
> switch, I don't feel it is accurate to say that "terminals on both the line
> AND load sides may be energized in the open position"...
More information about the RE-Wrenches