Hello Kirpal:
 
What is the relative age of these modules?  For starters....  Just curious.
 
Chris Daum
Oasis Montana Inc.
406-777-4309 local line
406-777-0830 fax
 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirpal
Khalsa
Sent: Wednesday, November 12, 2008 8:33 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Trouble Shooting Bad Diode


Bill and all.......So we were at the site today and these were our findings:
We covered each solar panel with cardboard 1 at a time.....we continued to
see the same lower voltage on string #2.  String #1 had an expected Voc.  
String 1 had a Voc of 368, String 2 had Voc of 312.  
We decided to disconnect the entire string.  Luckily the interconnects were
accessible without physically removing the modules.......I love array's that
are only 2 rows deep with service aisles all around.....
The system was 2 strings of 9 BP SX170's connected to a PVP2800XV.  
Module nameplate Voc was 44V.  Cell temp of the modules at time of
measurement was roughly 85-90 degrees F.  
all modules were in the 40.1-8 range....except module # 3 from the positive
homerun side was 38.8V, module 6 was 36.6V and module 8 was 10V.   
We had no trouble determining that module # 8 was defective......In these
modules I believe that the entire 72 cells are in a series.string...(am i
right?roughly .5+V per cell.).
Covering 1 module at a time did not give us any indication as to which panel
was defective.  The Voc with 1 module covered ranged from a low of 299VV to
a high of 304V. This did not make sense to me as to reducing the string Voc
from 312 to 304 by covering 1 module.........

Anyhow........the 2 modules that had reduced voltages......1 with ~38V and 1
with ~36V......would you consider those defective?  Worthy of trying to get
BP to warranty those?
We will be filing a warranty claim on the single panel that is obviously
defective.......
Thanks for your advice and input.....
Cheers,

Kirpal Khalsa
Renewable Energy Systems



On Fri, Oct 31, 2008 at 10:33 AM, Bill Brooks <billbrooks7 at yahoo.com> wrote:


Kirpal,

 

When you parallel, your voltages have to be the same, so you are correct in
that assumption.

 

Your assumption about the diodes is not correct. Diodes don't work like
that. You could have a shorted module (all three diodes shorted) which would
lower the Voc by one module. It looks like you have nearly two modules worth
of problems. It could be a total of 5 bad diodes, but that would be weird.
It could be you have a ground fault, and haven't tripped the GFP yet because
of lower sunlight levels-(it has to be very low sun to stay under 1 amp).
You also could have a wiring mistake, either because the factory reversed
wired a module (rare, but it happens)-that would be 2 modules low; or, you
could have skipped two modules somehow.

 

It does seem like a quarter of the bad string is out. Your assumption about
bad diodes could be correct, but it only affects the groups of cells its
connected to. Each diode protects 24 cells-it looks like you have 5 diodes
worth of loss. It could be in 2 modules, or up to 5 modules. 

 

The shading test is the best way to find bad diodes. Disconnect the bad
string from the good one and take a piece of cardboard the dimension of the
module. With your meter testing Voc on the back string, completely cover
each module, one at a time. When the Voc is not affected by complete shading
of a module, that module is completely bad. If the shaded module only loses
a portion of one module's Voc, then you have one or two, of the three
diodes, bad.

 

This is a great opportunity to learn how to troubleshoot a PV array. Take
the time, and the effort, to run through it carefully, learn the problems,
and report back with your findings. It's a beautiful thing to learn
something new.

 

Bill.

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirpal
Khalsa
Sent: Friday, October 31, 2008 10:43 AM
To: RE-wrenches
Subject: [RE-wrenches] Trouble Shooting Bad Diode

 

Greetings all......I was hoping i could have someone help me confirm a
troubled series string on a system we have installed.....
System consists of 16 BP 170 W 24V nominal modules......2 strings of 8
modules.....Vmp of each module is roughly 34V and Voc of each module is
roughly 41V.  One string is under-producing......String 1 Voc is 346V and
String 2 Voc is 272V.  String 1 Vmp under load is 270V and String 2 Vmp
underload is 270V.  I am hypothesizing that String 2 has a bad diode on the
3rd panel in and is reducing the Voc of that string by th 2 panels ahead of
it in the string.  I am hoping to figure this out without removing the
entire string and checking each panel if possible.....
I think the Vmp is equal due to the fact that both strings are paralleled in
the inverter and the 1st string is being pulled to the same level V as the
2nd string under load......Is my logic good?
Thanks for the help and advice.....
Cheers,




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org







-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20081112/f24c2ea0/attachment.htm>


More information about the RE-Wrenches mailing list