Pls explain "no additional relays required". I've done an ac-coupled system
and used a protective relay because I was told to do so at an Outback
workshop by your techs, because the Outback cannot regulate the AC charge
current coming from (in this case) the SunnyBoy string inverters. Is this
not the case?

 

Kirk Herander

Vermont Solar Engineering

802.863.1202

fax 802.863-7908

NABCEP(tm) Certified Solar PV Installer

Xantrex Certified Dealer Charter Member

NYSERDA-eligible installer

VT Solar Incentive Program Partner

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Christopher
Freitas
Sent: Sunday, November 09, 2008 1:31 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling

 

Thanks for the nice comment. 

 

AC coupling with the OutBack off-grid inverters and a typical batteryless
grid-tie inverter doesn't require any additional transfer switches or
protective relays - its actually pretty simple depending on how fancy the
battery charging regulation needs to be.  

 

It can be very cost effective and worth considering on any projects. 

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

 <mailto:cfreitas at outbackpower.com> cfreitas at outbackpower.com

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

 <http://www.outbackpower.com/> www.outbackpower.com

MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential,
and may also be protected by attorney-client or other privilege. If you
believe that it has been sent to you in error, please do not read it. If you
are not the intended recipient,you are hereby notified that any retention,
dissemination, distribution, or copying of this communication is strictly
prohibited.  Please reply to the sender that you have received the message
in error, then delete it. Thank you.
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20081110/2856e3e1/attachment.htm>


More information about the RE-Wrenches mailing list