[RE-wrenches] Actual losses from dissimilar orientations on single inverter
August Goers
august at luminalt.com
Fri Sep 12 10:38:17 EDT 2008
Wrenches -
The correspondence below brings up a question I've been pondering... What
are the actual losses due to differing string orientations on a single
inverter? Are there significant differences between the major inverter
manufacturers? What if we have a very steep roof facing East - West, would
we be better off with two inverters?
The well known Fronius white paper
(http://www.fronius-usa.com/worldwide/usa.solarelectronics/downloads/fronius
_ig_reaction_to_non_optimal_conditions.pdf) seems to indicate that losses
will be in the ~1% range. I took a SMA class a couple years back and they
indicated that the losses were probably closer to the 3% range, maybe even
more. Maybe things have changed by now, it would be great if some
manufacturer reps would chime in.
Does anyone have any data or solid info on this issue?
Looking forward to hearing the latest.
Best,
August
August Goers
Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
www.luminalt.com
august at luminalt.com
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Thursday, September 11, 2008 4:34 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] trouble shooting system with Sun Tie
Dana:
The failure mode of the original ST inverters were a failure in the MPPT
algorithm. The inverter would sweep the impedance too high until the
voltage would collapse. The inverter would then take several minutes until
it allowed the PV voltage to rise again. This would repeat throughout the
day resulting in a significant decrease in overall output. You could
witness this over any given half hour period.
Regarding arrays in dissimilar orientation: The loss due to differing
orientations should be about 1%, IF all modules in each string are facing
the same direction. This is because the different IV curves are of a
similar shape when superimposed on each other. The ST inverter might be
less able to average these curves and more susceptible to collapse.
Did you check the array fuses?
William Miller
At 03:23 PM 9/11/2008, you wrote:
>Hi all,
>
>I was called out this week to trouble shoot a system I didn't install.
>It's a five year old 1.44kW system with the following: Sun Tie ST 1500
>inverter and 12 Astro Power modules. It only produced 634kWh last
>year. With our sun here, the shading, orientation, equipment, etc. it
>should have produced around 1123kWh.
>
>I've heard a lot about Sun Tie failures, but don't know the details.
>What are the common failure modes? Is it likely that a failure of the
>Sun Tie would leave it operating, but only producing half what it
>should?
>
>When I showed up the system was producing 950W on a relatively sunny
>day - seemed pretty reasonable. After restarting the inverter it only
>produced around 150W. Is the MPPT very, very slow to find that sweet
>spot, or what was going on there?
>
>The system is comprised of three strings of 4 modules each. When I was
>there all three strings were producing about the same current, so that
>leads me to believe it's not a module failure.
>
>To make things more fun, the modules were installed at two different
>orientations. One string is at 38d slope, 30d east of true south,
>while the other two are at 36d slope, 75k east of true south. This
>certainly has a detrimental impact on the performance, but it doesn't
>seem to me that it could account for all of that energy loss.
>
>Thoughts?
>
>Thanks a lot!
>
>Dana
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list