Max,
I agree with the previous comments regarding likely issues to pursue with
this system.
Mr. Undercuffler mentioned temperature compensation as a piece to the
puzzle. I was recently troubleshooting a system where there was a large
difference between actual and compensated voltages with a SW Plus. The SW
Plus uses actual voltage to make decisions regarding generator starting
(Xantrex tech support didn¹t have a known reason for this), which led to
premature generator starting (and LBCO shutoff) when the batteries were
warm. It may be worth checking on which voltage (compensated or not) the XW
uses to make these types of decisions.
P.
Phil Schneider
Creative Energies
--- On Mon, 8/18/08, Max Balchowsky <max at seesolar.com> wrote:
> From: Max Balchowsky <max at seesolar.com>
> Subject: Re: [RE-wrenches] offgrid system question
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Monday, August 18, 2008, 3:00 PM
> Dear wrenches, going to look at a system installed by others
> and would like some input from some of you with more off
> grid experience than I have ( 4 systems over the years). the
> system was put on a new home - off grid 20 sharp ND123UJF
> panels 4 modules in series - 5 parrallel strings, 2460 total
> array dc voltage. mppt 60-150 charge controller, 12 sun
> extender sealed AGM batteries, 305 AH at 12 vdc, wired for
> 915 AH at 48 volt DC. The system is tripping off when the AC
> unit trys to start - AC is comfortmaker 3.5 ton 13 seer.
> They say start up inrush is 104 amps (sounds high to me) and
> they put a DST 10 soft start on the unit (I think that's
> just a big capacitor). I haven't been on site yet but it
> sounds to me that they just didn't design enough
> inverter capacity into the system...... What are your
> thoughts?
>
> Max Balchowsky
> SEE Systems
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list