[RE-wrenches] Imbalanced Legs in 3-Phase systems
Ryan Mayfield
ryan_mayfield at earthlink.net
Fri Aug 8 18:40:07 EDT 2008
Jeff,
My memory also recalls something about a 6kW value.
I've talked to one of our local utilities about this as well and they base
the accepted imbalance by the size of the transformer serving the building.
I have never read their white paper on the subject though. When I described
a similar situation for an install we were working on, the engineer
acknowledged that he would not have any concern with such an arrangement.
You may approach your utility and see if they have a standard protocol you
could follow for your system.
Ryan
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Jeff
Clearwater, Village Power Design
Sent: Thursday, August 07, 2008 10:14 AM
To: RE-wrenches
Subject: [RE-wrenches] Imbalanced Legs in 3-Phase systems
Hi Wrenches,
How does one determine how much imbalance can be tolerated on a 3 phase
system?
I'd like to feed 2 SMA SB5000s at 277 VAC into a 480 VAC panel
instead of 1 13 KW Solectria at 480VAC as the PV system is only 9500
Watts STC. The main on the backfed service panel is 600 A. But I'm
not that sure of the loads as it's new construction and hasn't been
characterized.
What are the appropriate calcs to do here?
Thanks!
Jeff C.
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer
Voice: 413-259-3776
Fax: 413-825-0703
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
_______________________________________________
List sponsored by Home Power magazine
RE-wrenches at lists.re-wrenches.org
http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.12/1597 - Release Date: 8/7/2008
5:54 AM
More information about the RE-Wrenches
mailing list