[RE-wrenches] Gray code area

Drake Chamberlin drake.chamberlin at redwoodalliance.org
Thu Jul 31 22:53:23 EDT 2008


Bill,

That is a great point.  As it stands, the box 
ahead of the residence does contain a main 
breaker.  If we get rid of that breaker and turn 
it into a lugs only panel, it would satisfy the 
requirements.  I wonder how that would pan out, 
since the wiring runs through this other building.

Thanks,

Drake


At 12:49 PM 7/31/2008, you wrote:
>Content-Type: multipart/alternative;
>         boundary="----=_NextPart_000_006F_01C8F303.83492700"
>Content-Language: en-us
>
>Drake,
>
>690.64 relates everything to the service 
>disconnects. All the rest of this is semantics. 
>As long as the PV connection is upstream of the 
>service disconnect (i.e. in between the service 
>disconnect and the service meter), it is 
>considered a line side service connection.
>
>If there is no way to turn off the residential 
>service in the panel with the “feed-thru” lugs, 
>there is no service disconnect for the 
>residential service yet. That way if the 
>connection were on the line side of the first 
>service disconnect for the residence (one of two 
>services at the site, both coming from the same 
>service drop­to get all the semantics proper), 
>it is considered a line-side connection. So what is it
.?
>
>Bill.
>
>From: re-wrenches-bounces at lists.re-wrenches.org 
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] 
>On Behalf Of Drake Chamberlin
>Sent: Thursday, July 31, 2008 9:13 AM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] Gray code area
>
>At 03:24 PM 7/30/2008, you wrote:
>
>According to the two paragraphs above, the 
>commercial building has two commercial 
>services???  One will receive PV and one will not??
>
>One service is for the commercial building and 
>one is for the residence.  There is one service 
>drop to two meters.  Both services will be fed PV.
>
>
>Drake Chamberlin
>Athens Electric
>OH License 44810
>CO License 3773
>740-448-7328
>303-328-5533
>_______________________________________________
>List sponsored by Home Power magazine
>
>RE-wrenches at lists.re-wrenches.org
>
>http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>http://www.re-wrenches.org/etiquette.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
303-328-5533 