620 VDC [RE-wrenches]
Joel Davidson
joel.davidson at sbcglobal.net
Fri Jun 27 11:26:09 EDT 2008
<x-flowed>
Drake,
Uni-Solar and other amorphous silicon solar cells have a flatter IV curve
than crystalline silicon cells which requires a wider inverter input voltage
window. This means that it is difficult to design a Uni-Solar PV system for
places like Boston where cell temperatures can range from -25C to +70C. Cell
temperature right before daybreak is almost always the same as ambient
temperature unless the building leaks a lot of heat.
Joel Davidson
----- Original Message -----
From: "Drake Chamberlin" <Drake.Chamberlin at redwoodalliance.org>
To: <RE-wrenches at topica.com>
Sent: Friday, June 27, 2008 8:35 AM
Subject: RE: 620 VDC [RE-wrenches]
>
> Thank you all for your input. It appears that this is an area that needs
> work in the Code. I'm looking forward to Bill's new temperature guidance
> being implemented.
>
> With the particular system we are considering, we would be using Uni-Solar
> laminates that will adhere directly to a metal roof. Is there anyway we
> can get credit for the building heat that will never let the modules get
> down to the ambient?
>
> Drake
>
>
> At 11:39 PM 6/26/2008, you wrote
>
>>Joel,
>>
>>What does 600-Volts nominal mean to you? As Drake pointed out, 600Vac has
>>a
>>peak voltage of 850V. Any momentary exceeding of 600V, when using
>>reasonable
>>statistical design numbers, will be momentary at best and have no affect
>>on
>>the equipment unless the equipment is faulty to start with.
>>
>>Bill.
>>
>>-----Original Message-----
>>From: Joel Davidson [mailto:joel.davidson at sbcglobal.net]
>>Sent: Thursday, June 26, 2008 6:43 PM
>>To: RE-wrenches at topica.com
>>Subject: Re: 620 VDC [RE-wrenches]
>>The NEC is very specific about 600 volts DC and AC in Chapter 1, paragraph
>>2. The 600-volt Rule is that fundamental. Almost all AWJ and Code Priests
>>interpret Article 690.7 "lowest expected ambient temperature" as the
>>lowest
>>temperature recorded by their chosen Weather Scribes even if that low
>>temperature only happened once many years ago. From a practical
>>standpoint,
>>some solar modules can not be used optimally with some inverters. Every
>>time
>>
>>I get a good module/inverter match, the manufacturers change specs,
>>availability, price, or all three.
>>
>>----- Original Message -----
>>From: "Drake Chamberlin" <Drake.Chamberlin at redwoodalliance.org>
>>To: <RE-wrenches at topica.com>
>>Sent: Thursday, June 26, 2008 12:37 PM
>>Subject: 620 VDC [RE-wrenches]
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list