25 kW inverter [RE-wrenches]
Paul Israel
paul at sunlightsolar.com
Thu Jun 12 16:18:07 EDT 2008
Wrenches,
1. Most Utility Interconnection Applications use the inverter nameplate to
determine system size for interconnection.
2. The NEC uses it to size the OCPD.
3. The manufacturers vary as to which inverter can handle power above the
nameplate rating. Some will process the extra power others will not.
However, by the time we follow the manufacturers or figure for ourselves how
much wattage the inverter can efficiently process we are probably darn close
to the rated nameplate. Time, that stringent beast, will limit it anyway.
4. Oversizing an inverter for future expansion would limit us to installing
a 25kW inverter. Installing a 50kW inverter and then putting 25kW of panels
would be questionable at best. A loophole that would be quickly closed.
Hey, let's just change the law!
Paul N. Israel, President
paul at sunlightsolar.com
www.sunlightsolar.com
541/389-3480 (Oregon)
203/878-9123 x103 (CT)
860/617-6527 (Cell)
-----Original Message-----
From: Jeff Oldham [mailto:starpower4u at juno.com]
Sent: Thursday, June 12, 2008 12:48 PM
To: RE-wrenches at topica.com
Subject: Re: 25 kW inverter [RE-wrenches]
For sure don't use Inverter nameplate as pointed out, however it will see to
it that you do not exceed the AC by much. I say "much" as most of us have
seen an inverter exceed nameplate more then a few times for short periods.
At the same time I can't see any engineering review assume it will exceed
nameplate. I'm not sure if the CSI calculator will accept out of State Zips
or not. If it does you will error on the safe side as the calc is a bit
optimistic by 5-15% depending on site conditions and equipment. Another
approach is to use the online inverter manufacturers calculators and plug in
your temperature ranges. Here it tends to be a bit conservative depending on
the manu. If you add 10% to their output numbers you should be safe.
Finally pick a hazy day for your inspection (just kidding!).
Good luck,
-jeff
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative
SOLutions
____________________________________________________________
Paying too much credit card interest? Find low APR credit cards. Click here.
http://thirdpartyoffers.juno.com/TGL2131/fc/Ioyw6iifRpSU02zNZhkKWyucFtiehQr7
WXyHSUy3jSyaInC4V8DuVo/
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list