Outback MX problem [RE-wrenches]

Ron Young solareagle at solareagle.com
Wed May 28 15:15:39 EDT 2008


<x-flowed>

I'm having a problem with an Outback MX going into sleep mode and  
showing incorrect voltage on the input. It's a single 3524 inverter  
with a 4KS25 Surrette battery charged by a Whisper 100 and a 680 watt  
array (Evergreen 170's) wired in two strings for 48v. The only time  
the MX will charge is if a charge is initiated via FORCE BULK mode or  
if the customer turns on her vacuum cleaner and it draws down the  
batt. voltage then the MX kicks in. She says she sees the pv output  
voltage drop from 70 (sunny day) to as low as 24 then start building  
up again. If it stays around 60 then the MX keeps charging but once  
it gets back up to 70 then MX cuts out. Bulk set point is at 29.4.

Actual battery voltage measured at the terminals is 25.1 today but  
the MX says 29.1.

Outback wants to replace the unit but I'm not convinced yet that it's  
defective, just wondering if maybe something else is going on that  
I've overlooked. The above behaviour is the same whether there is  
wind or no wind so I've ruled out a conflict with the Whisper  
controller.

Ron Young


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------

</x-flowed>


More information about the RE-Wrenches mailing list