We are doing an installation with 2 Sunny Boy 5000 inverters each
requiring a 30 amp 2 pole breaker. The closest point of
interconnection is outside the house on the supply side of the main
service disconnect near the customer side of the utility meter.
According to 690.64B on the load side we are limited to 120% of the
busbar rating, which means we could not put 2- 30 amp backfeed
breakers in the main 200 amp service panel. But 690.64A does not
state a limitation of 120% . So we are considering a 200 amp feed
through panel, also recommended by our local electrical inspector,
and then putting our 2-30 amp 2 pole breakers in this feed thru
panel. Anyone have any comments on this method? What other methods
are people using to make a supply side interconnection?
Larry Brown
Sun Mountain
- - - -