Hi Steve,
William' approach is exactly it. We use to do 1% at Vmp but as
copper prices increased we did a more careful analysis of the peak vs
average issue and now use 1.5% But as he says make sure that's from
panel to inverter, not just from combiner to disconnect. I do take a
look at Vmin (the inverter's MPPT min) for the worst case scenario
but that usually doesn't go over 2% if Vmp is at 1.5% or better.
That said if the run is short or the pull easy I tend to bump up a
size to maximize those precious PV watts which usually puts me back
in the 1% range at Vmp - but if the run is long and the cost starts
going up - William's perspective is what we use.
Hope that helps!
Jeff Clearwater
Village Power Design
>Steve:
>
>I'd say E because high temp Emp will occur at lower output amperage.
>I doubt the difference between D or E will be significant and Voc
>does not count.
>
>Consider this concept: Rated current occurs rarely, if ever.
>Assume, though, it occurs at noon. The rest of the day presents
>varying degrees of lesser current. What is the area under the
>curve? My research indicates it is 50% of the peak amperage.
>
>What does this mean? It means that if you design a PV feeder for 2%
>voltage drop at peak output, it will average 1% over the day. Or,
>design criteria for PV feeders is only half as important as we think
>it is. (Don't forget to quantify cumulative loses throughout all
>feeders and components, however.)
>
>William Miller
>
>
>At 10:18 PM 4/30/2008, you wrote:
>>I have a 400 foot run on an output circuit to combiner, 23.5 amps.
>>Should the DC VOLTAGE that is used as the system voltage to calculate
>>voltage drop be:
>>A) Voc at low temperature
>>B) Voc at high temperature
>>C) Nameplate Voc
>>D) Vmp at high Temperature
>>E) Nameplate Vmp
>>
>
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer
Voice: 413-259-3776
Fax: 413-825-0703
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list