XW generator start question [RE-wrenches]

Jay Peltz, Peltz Power jay at asis.com
Fri Apr 25 12:27:34 EDT 2008


<x-flowed>

Hi Mark,

is this upgrade now standard, and if not, how hard is it to install?

thanks,

jay
On Apr 25, 2008, at 8:57 AM, Mark Edmunds wrote:

>
> Hi Dan, Jay
>
>
> You have the correct information Dan - the original design did need  
> the
> "run" signal, even with 2 wire units - the software upgrade we now  
> have
> will allow the system to look at the AC2 voltage to determine that the
> generator is running so it can be a true 2 wire installation.
>
> Cheers,
>
> Mark
>
>
>
> Mark Edmunds
> Xantrex Technology Inc.
>
>
> -----Original Message-----
> From: Dan Rice [mailto:danrice at scinternet.net]
> Sent: Friday, April 25, 2008 12:08 AM
> To: RE-wrenches at topica.com
> Subject: Re: XW generator start question [RE-wrenches]
>
>
> Jay,
>
> Yes, the GSM is required to interface a generator to the XW, 2-wire
> start or otherwise. The GSM also requires a "generator running" signal
> in order to recognize a running generator and hold the 2-wire signal
> "on". The GSM "run"
> sensor circuit requires a 12 volt nominal (30 volts max) signal  
> from the
> generator, and requires another 2 wires between the generator and the
> GSM, so for a "2-wire" start generator, actually 4 wires are required.
> Xantrex has heard the complaints about this loss of a true 2-wire  
> start
> feature on the XW, and I understand that there's a software upgrade
> available that will allow the GSM to recognize when there's AC line
> voltage present at the AC input terminals of the inverter (AC 2 in, I
> assume). This should eliminate the need for the 12 volt "run" signal
> (and the extra 2 wires) from the generator to the GSM. I haven't tried
> this upgrade myself. On the one installation I've worked on, I ran the
> additional 2 wires, and piggy-backed off of one of the propane  
> solenoids
> for the 12 volt "run" signal. The GSM works fine this way.
>
> I hope that helps.
>
> Dan Rice
> Abundant Sun, LLC.
>
> ----- Original Message -----
> From: "Jay Peltz, Peltz Power" <jay at asis.com>
> To: <RE-wrenches at topica.com>
> Sent: Thursday, April 24, 2008 7:20 PM
> Subject: XW generator start question [RE-wrenches]
>
>
> |
> | HI All,
> |
> | Do you need the generator start module to control a 2 wire start
> | generator on the XW inverter?
> |
> | thanks,
> | jay
> |
> | peltz power
> |
>
>
>
> - - - -
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list