Jay,

Yes, the GSM is required to interface a generator to the XW, 2-wire start or
otherwise. The GSM also requires a "generator running" signal in order to
recognize a running generator and hold the 2-wire signal "on". The GSM "run"
sensor circuit requires a 12 volt nominal (30 volts max) signal from the
generator, and requires another 2 wires between the generator and the GSM,
so for a "2-wire" start generator, actually 4 wires are required. Xantrex
has heard the complaints about this loss of a true 2-wire start feature on
the XW, and I understand that there's a software upgrade available that will
allow the GSM to recognize when there's AC line voltage present at the AC
input terminals of the inverter (AC 2 in, I assume). This should eliminate
the need for the 12 volt "run" signal (and the extra 2 wires) from the
generator to the GSM. I haven't tried this upgrade myself. On the one
installation I've worked on, I ran the additional 2 wires, and piggy-backed
off of one of the propane solenoids for the 12 volt "run" signal. The GSM
works fine this way.

I hope that helps.

Dan Rice
Abundant Sun, LLC.

----- Original Message ----- 
From: "Jay Peltz, Peltz Power" <jay at asis.com>
To: <RE-wrenches at topica.com>
Sent: Thursday, April 24, 2008 7:20 PM
Subject: XW generator start question [RE-wrenches]


|
| HI All,
|
| Do you need the generator start module to control a 2 wire start
| generator on the XW inverter?
|
| thanks,
| jay
|
| peltz power
|
|
| - - - -
| Hosted by Home Power magazine
|
| To send a message: RE-wrenches at topica.com
|
| Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
|
| List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
|
| Check out participant bios: www.mrsharkey.com/wrenches/
|
| Moderator: michael.welch at homepower.com
|


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list