Matt, et. al:
This is a high-voltage, low-amperage system--unfortunately.
Tomorrow, we are "correcting" all of the other "issues" the inspector noted,
and awaiting responses from Grundfos and a Washington State Grundfos
distributor (with not much hope of resolution).
Hmmm. Installing a "standard AC" pump for the inspection . . . Do you mean
an AC pump and inverter with UL listing? How does this make sense with a DC
solar array and no inverter? The inspector is savvy enough to see through
this ruse.
I will keep you wrenches posted, but I think this will be a disaster for us
and our client unless the inspector, by some miracle, changes his mind and
accepts the CE rating in the Grundfos literature.
Bob Clark
SolarWind Energy Systems, LLC
bclark at solar-wind.us
No virus found in this outgoing message.
Checked by AVG.
Version: 7.5.524 / Virus Database: 269.23.1/1384 - Release Date: 4/17/2008
3:47 PM
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list