Hello Wrenches,
I've been reading the 2008 code and talking to an inspector who is
studying 690 very thoroughly. A question arises about the grounding
conductor between the AC service panel and the inverter. Is it an
equipment grounding conductor or a grounding electrode conductor, or both?
It would need to be both if there were both AC and DC systems. This
is covered in 690.47(C), "Systems with Alternating-Current and
Direct-Current Grounding Requirements." Unless the array had plastic
frames, it would seem that there would always be DC grounding
requirements, so what does this mean?
This is direct grid tie with no DC loads. It seems another section
would need to be added to deal with a direct grid tie system.
The main issue that arises from this is that if the ground wire is
considered a grounding electrode conductor, it needs to be #8. This
would mean that a 10/3 WG cable would need to have a separate ground
wire run that is at least #8. It would probably be easier to run a
#6 since it can be run of the surface.
How have you and your inspectors been interpreting this?
Thanks,
Drake
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list