Testing GFCI's [RE-wrenches]

Nick Lucchese nickl at sierrasolar.com
Wed Mar 26 15:07:49 EDT 2008


<x-flowed>


-- 
Greetings Wrenches,

I recall this issue being brought up before but couldn't find it. My 
apologies to those frustrated by my unsuccessful attempt at locating 
it in the archives. I have an installation 1.5 hours away and just 
received a phone call from the customer after being visited by the 
inspector. For now it's a single FX on an E-panel with a string of 
4-L16's, PV to be added later. There is utility present although the 
customer has just one 20 amp circuit running from the main service 
box 200' away. Neutral to ground bond occurs after E-panel in main 
load subpanel. Presently he is running the entire house (just his 
tools for construction) on this single 20 amp circuit from the 
utility while he builds the house. When the inspector uses his GFCI 
tester with the E-panel in inverter bypass mode (utility) everything 
checks out okay and the GFCI trips. Once the utility is removed from 
the equation and in stand alone mode/ inverter power the tester says 
that the neutral and hot wires are reversed and the GFCI's won't 
trip. Does anyone recall why this is and what type of GFCI tester 
could be used to verify that the GFCI's are working properly? The 
inspector had truly convinced him that the hot and neutral output 
wires were reversed so I got the customer to open up the E-panel to 
trace the wires and confirm that in fact everything is wired 
correctly. I'd really like to understand how this can happen so that 
the customer can get his final and out of his higher interest 
construction loan by the end of the month. Any insights?

Thanks for your time,



Nick A Lucchese


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




</x-flowed>


More information about the RE-Wrenches mailing list