Misleading fault indications [RE-wrenches]

Mark Frye markf at berkeleysolar.com
Fri Feb 29 12:08:28 EST 2008


William,

The fault condition is a ground fault. Why is it that the tripped GFI
breaker must only indicate a PV ground fault?  The ground - negative bond is
the bond that serves the PV and the battery/inverter circuits, so why should
the tripped breaker not indicate a ground fault in either circuit?
 
Mark Frye
Berkeley Solar Electric Systems
271 Vistamont Dr
Grass Valley CA 95945
(530) 401-8024
www.berkeleysolar.com
 
-----Original Message-----
From: William Miller [mailto:wrmiller at charter.net] 
Sent: Thursday, February 28, 2008 11:21 PM
To: RE-wrenches at topica.com
Subject: Misleading fault indications [RE-wrenches]


Colleagues:

We have been installing a number of off-grid systems which include the 
Outback GFI breaker assemblies.  This is multi-pole breaker has one 0.5 amp 
pole which is connected between the ground and neutral busses.  This 0.5 
amp pole replaces the wire that usually bonds the ground and negative 
busses together.

I wonder if removing this bonding wire causes another problem.  That 
problem is illustrated in the following link  Click on the second case, 
"Misleading ground fault indication:"

http://mpandc.com/case_studies/ground_fauilt/ground_fault.html

I am interested if anyone else sees this problem or has wondered about 
this.  I am hoping I am just seeing it wrong.  If I'm right, there are some 
serious implications.  I appreciate your opinions on this.

William Miller



-- _________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600     Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list