Inverter meters; was Batteryless inverter recommendation [RE-wrenches]
Brad Bassett
bbassett at hei.net
Wed Feb 27 11:24:38 EST 2008
Thanks Jeff for bringing up those good points Matt came up with.
1. Check
2. Meter is on output of inverter only so, SB is about PF 1 right?
3. Check ditto above and only goes one way.
4. Check
5. One of them is still wrong.
Also there was talk a while back about some kWh meters not being very
accurate below 200 watts, but I think that was mostly in mechanical
meters being a little sticky, and this is a digital meter.
Brad
AEE Solar
Jeff Clearwater, Village Power Design wrote:
>
> I've brought this to the attention of the List in the past (See 5/18/
> - 5/20/06 - KWH meter discrepancy). Matt replied with a very
> complete list of possible causes (below).
>
> We do really need to get to the bottom of it. Any more thoughts or
> updates since May of '06 Matt? Others?
>
> Best,
>
> Jeff Clearwater
> Village Power Design
>
> At 10:04 AM -0700 5/20/06, Matt Lafferty wrote:
> >Wrenches,
> >
> >I see a couple of things "missing" from the descriptions in this thread
> >for
> >a conclusive determination of the true cause for the discrepancies...
> >
> >1) Hours of operation. In many cases, even though it is generally
> >"prohibited", the PV systems will have a number of hours or days
> >"head-start" on the PV Generation Meters. I've seen numerous cases
> >where
> >this accounts for over a month of production on the inverters by the
> >time
> >the PV Meter is installed. If your comparisons have been made on
> >relatively
> >new systems, there is a good chance some of your discrepancy is related
> >to
> >this. It is important to take a reading on both meters at the same
> >time,
> >then take another reading some time later for proper comparisons. The
> >longer the time interval between readings, the more accurate your
> >comparison
> >results will be. (I'm not saying they will be identical by any means.)
> >
> >2) Most revenue grade kWH meters account for power factor losses to some
> >degree. What this means is that a site with a low power factor actually
> >"uses" more energy to do the same "work" as far as the meter is
> >concerned.
> >This is a double-bite for our purposes... The Customer is paying for kWH
> >that they wouldn't need if the PF was 1.00 and their PV Meter is
> >recording
> >the opposite effect. This occurs regardless of whether the low power
> >factor
> >is "incoming" or "site-caused. I can't speak for the Inverter Manus, but
> >my
> >observations, testing, and comparisons have led me to the conclusion
> >that
> >their metering does not account for this as accurately as revenue grade
> >kWH
> >meters. (Note: It is common for utilities to deny this and/or claim
> >that
> >the low PF is caused by the Customer. I've seen them claim that they
> >are
> >"losing revenue" because of this issue.)
> >
> >3) Most revenue grade kWH meters are very accurate in the "forward"
> >direction (+/- .5%), but wildly vary in their accuracy when running
> >"backward". This aspect is huge on a number of fronts and there isn't
> >room
> >to describe the plethera of scenarios here. You may be wondering "why
> >would
> >my PV meter run backward?"... Simple. At nite, the inverter uses some
> >AC
> >power... A very small amount based on the Manus, but some nonetheless.
> >It
> >is impossible to tell here what that effect has on the "dial readings".
> >The
> >Inverter displays do not count this. For starters, you will have to
> >know
> >whether or not the PV meter is detented or non-detented. After that you
> >will have to find out whether or not it is calibrated to meter
> >"bi-directional" or not and the accuracy tolerances for both. Good luck
> >getting that info!
> >
> >4) If you have a 120V Inverter, you need a 120V meter to properly meter
> >it.
> >Running the noodle through one leg of a 240V meter will not provide
> >accurate
> >results. Period.
> >
> >5) Electro-mechanical vs. "calculated". This is another spot where the
> >differences get wild. Your PV Meter is most likely EM. Inverter
> >displays/meters are calculated. The circuitry & programming in the
> >Inverters uses "constants" in order to "do the math". Contact your
> >Inverter
> >Manu for specifics related to their methodology. Be sure to let us all
> >know
> >what you find out! (Hint: This is very closely related to #2 above.)
> >
> >Here are the high-points of my testing and research over the years:
> >
> >After eliminating #1 & #4 above, the largest discrepancy factor is a
> >combination of #2 & #5. Once you've isolated and quantified them,
> >multiply
> >the Inverter meter reading by the average Power Factor. You will be
> >amazed
> >how closely the result comes to matching the PV Meter reading.
> >
> >How to go about doing it:
> >
> >In order to track this, you'll have to get your hands on a recording
> >analyzer that does power factor measurements. (I.E. Fluke 43 or
> >similar...
> >~$2K) If you don't have one, and most of us don't, it is possible to
> >request
> >a "power quality" or "meter accuracy" test from your utility company.
> >
> >Generally they all do this at no charge. You will have to tell them
> >specifically what aspects you want results for and the interval that
> >measurements are taken... Try to talk directly to the Power Quality Tech
> >and
> >let him/her know what you are trying to do. They are generally pretty
> >laid
> >back and quite helpful if you aren't pushy or "blaming the big bad
> >utility".
> >They will let you know what they can measure/record at what intervals
> >and
> >for how long. Generally speaking, the more channels you want measured
> >reduces the length of time and increases the interval period for your
> >test.
> >After you get a decent relationship going, be sure to try to get the
> >"data"
> >as well as the standard "report". Ask for it in a CSV or spreadsheet
> >format. This may or may not be possible due to "policy". Generally
> >speaking, you will get a lot more bees with honey, so be sure to have
> >jelly
> >donuts on hand. Your attitude will play a large part in determining how
> >all
> >this goes. If you know you can't be civil with them, send somebody who
> >can!
> >(Hint: "Awww shucks" and "Golly gee" and "I didn't know that... Wow!
> >Thanks!" will get you a long ways toward your goal... These guys are
> >"tech-heads" by nature and they can talk way over your head in most
> >cases...
> >Way over mine, anyway. The "Awww shucks" thing plays nicely in getting
> >the
> >conversation onto a "plain English" level.)
> >
> >Some utilities have power quality recorders available to Electrical
> >Contractors on a loaner basis for use in their service territories.
> >Check
> >into this option.
> >
> >OK. Off to spend the rest of the weekend campin at a Hot Springs. Have
> >a
> >good one, ya'll!
> >
> >Pray for Sun! (I'd prefer not to have my sleeping bag soaked)
> >
> >Matt Lafferty
> >Universal Energies Institute
> >mlafferty at universalenergies.com
> >(415) 252-0343 Phone
> >(916) 914-2247 Fax
> >
>
>
>
>
> >I now have a few weeks of time on my SB700 system that also has a
> >utility owned digital revenue meter on it. So far the SB meter reads
> >145% of the revenue meter reading.
> >
> >Brad
> >AEE Solar
> >
> >
> >Joel Davidson wrote:
> >
> >>
> >> I have 20 Siemens SP75 modules feeding into an SB2100U inverter and a GE
> >> I70
> >> kWh meter. From September 20, 2007 to February 22, 2008 the SB2100U
> >> measured
> >> 740.2 kWh and the GE I70 measured 736 kWh. (PVWATTS estimates 748 kWh at
> >> 81%
> >> DC-to-AC derate.) Looks good to me.
> >>
> >
> >
> >
> >- - - -
> >Hosted by Home Power magazine
> >
> >To send a message: RE-wrenches at topica.com
> >
> >Archive of previous messages:
> >http://lists.topica.com/lists/RE-wrenches/read
> >
> >List rules & how to change your email address:
> >www.mrsharkey.com/wrenches/etiquette.php
> >
> >Check out participant bios: www.mrsharkey.com/wrenches/
> >
> >Moderator: michael.welch at homepower.com
>
>
> --
> ~~~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> Sustainable Energy & Water Solutions for Home & Village
> http://www.villagepower.com
> gosolar at villagepower.com
> NABCEP (tm) Certified Solar PV Installer
>
> Voice: 413-259-3776
> Fax: 413-825-0703
> 65 Schoolhouse Rd
> Amherst, MA 01002
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
Brad Bassett
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list