Calculating string amperages [RE-wrenches]
William Miller
wrmiller at charter.net
Tue Feb 26 19:59:18 EST 2008
<x-flowed>
Ray, Colleagues:
I have been scratching my head ever since Ray sent me the e-mail below. I
was very certain that at one point in time I had been convinced by a
Fronius engineer that 3 strings of Solar World modules are allowed without
fusing. When Ray sent this e-mail, rechecked my calculations and found
that they do not work.
Just now I realized that Solar World changed the specified series fuse
ratings sometime in the recent past. In 2006 and before, the SW175 had a
series fuse rating of 20 amps, which allowed the three strings
((3-1)*5.3*1.56<20). I actually found a photo of a module label if anyone
really needs documentation on this.
The series fuse rating now is 15 amps and three strings are not
allowed. Two strings are allowed.
I apologize, Ray, for leaving this hanging. My memory is not what it used
to be.
William
At 11:11 AM 2/8/2008, you wrote:
>Well we do have some discrepancies here. William was saying we could
>go to 3 parallel Solar World strings, John Berdner here says only
>one, and I'm still saying 2 is good.
>John I have 2 issues with your excellent analysis.
>1) 690.8 B) (1) exception: "Circuits containing an assembly, together
>with its overcurrent device(s), that is listed for continuous
>operation at 100% of its rating shall be permitted to be utilized at
>100% of its rating."
>This means that with the right breaker, we don't have to use the 1.56
>multiplier for array current, only 1.25 which is for edge of cloud
>effect, etc. I have seen Solar world modules exceed their nameplate
>rating, so this multiplier is appropriate.
>2 x 5.1 A x 1.25 = 12.75 Amps on a 15A breaker that is rated for 100%
>duty is acceptable. (most Outback and Midnite solar offerings are
>100% rated BTW)
>
>
>R. Walters
>Solarray.com
>NABCEP # 04170442
--
This message has been scanned for viruses and
dangerous content by MailScanner, and is
believed to be clean.
This e-mail has been scanned for SPAM and virus infections using
Barracuda.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list