2% current (6 hr) is text book for 100% SOC and very accurate. Of course, getting the client to run the gen that long, as you know, is the hard part.
Regards,
Jamie
>>> "Jay Peltz, Peltz Power" <jay at asis.com> 13/02/2008 12:57 pm >>>
Hi Jamie,
I have heard other battery manufactures use a 2% current rate to end
absorb charge.
( 400 amp hr battery X 2% = 8 amps)
What do you think about this vs a set time for absorb?
thanks,
jay
peltz Power
On Feb 13, 2008, at 8:51 AM, James Surrette wrote:
>
> Hello William,
>
> A quick note from the battery supplier side.
>
> We've noticed, as battery banks capacity has increased, an increase
> in deficit cycling and an increase in the need of "corrective"
> equalizations. However, a quick calculation that we've been
> providing, which has shown good success;
>
> i) At bulk voltage - assume battery at 80% SOC
> ii) Take 20hr rate capacity and determine AH of remaining 20% deficit.
> iii) Divide AH deficit by the "average" charge current during the
> Absorb cycle - not an exact science I know.
> iv) Provides a more accurate required absorb time - and often
> surprised the client when 4+ hours are required.
>
> EQ duration can be calculated in the same fashion.
>
> Regards,
>
> Jamie
>
>
>>>>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
<br><br>This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content.
<br><br>The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list