trojan battery cycle [RE-wrenches]
James Surrette
james at surrette.com
Wed Feb 13 11:51:42 EST 2008
Hello William,
A quick note from the battery supplier side.
We've noticed, as battery banks capacity has increased, an increase in deficit cycling and an increase in the need of "corrective" equalizations. However, a quick calculation that we've been providing, which has shown good success;
i) At bulk voltage - assume battery at 80% SOC
ii) Take 20hr rate capacity and determine AH of remaining 20% deficit.
iii) Divide AH deficit by the "average" charge current during the Absorb cycle - not an exact science I know.
iv) Provides a more accurate required absorb time - and often surprised the client when 4+ hours are required.
EQ duration can be calculated in the same fashion.
Regards,
Jamie
>>> William Miller <wrmiller at charter.net> 13/02/2008 12:27 pm >>>
Friends:
I have been monitoring a 1 year old set of IBE 85N-33 batteries in a quad
stack Outback system we installed. With factory settings for EQ duration,
the bank EQs in 2.5 hours and leaves the specific gravity well below full
charge. We are now setting the EQ and the absorption duration for minimum
3.0 hours for L-16 systems, and we will longer for large form batteries.
Has anyone else monitored short charge durations for the EQ and absorption
on Outback equipment?
William Miller
At 08:05 AM 2/13/2008, you wrote:
>I have heard this from others and it always makes me curious as my
>customers easily get 8 to 12 years out of L-16s. Perhaps it is common for
>some L-16's to not get fully charged after use? I tend to set the charge
>controller a bit on the high side and now that the MX-60 has an auto
>equalize option, I set it up to EQ once a month and tell the customer to
>judiciously watch the water levels. As long as they do not go dry, these
>batteries seem very robust for off grid and on grid w/ backup use.
>
>Todd
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
<br><br>This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content.
<br><br>The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list