Rinnai boiler controller [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Tue Feb 5 19:41:21 EST 2008
Kirk -
I have seen problems with these before as well - they are extremely
sensitive. They seem to work fine on the OutBack inverters but we have
had reports of problems with them when the generator is running and the
charger is pulling power. This customer even turned off the OutBack's
charger and had issues when he connected a IOTA charger to the generator
as well. I think it was a particularly flakey generator - but that
still seems pretty extreme.
We did work up a filter for the customer as a favor to the dealer - who
is not on the wrenches list - but I know it did draw some idle power and
was not particularly efficient. The filter was similar to a ferro /
constant voltage transformer - which are available off-the-shelf which
might work.
Here is a link to some I used years ago with SWs and oil-fired furnace
controllers:
Sola -
http://www.solaheviduty.com/products/powerconditioning/mcr_port.htm
General information - http://en.wikipedia.org/wiki/Voltage_regulator
Warning - they do make some noise and get warm all the time they are
on...
I hope this helps!
Christopher
Christopher Freitas
Director of Research of Development
OutBack Power Systems, Inc.
cfreitas at outbackpower.com
Tel 360 435 6030
cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com
-----Original Message-----
From: Kirk Herander [mailto:kirk at vtsolar.com]
Sent: Tuesday, February 05, 2008 7:40 AM
To: RE-wrenches at topica.com
Subject: Rinnai boiler controller [RE-wrenches]
I have a situation were a Rinnai wall-mounted boiler occasionally shuts
down. Its controller indicates a line frequency error. This is off-grid,
-2-
Xantrex 4048 inverters w/15kw generator backup.
Nailing it down to coincide w/generator turn on/off, load variation,
Xantrex
waveform steps, ect. is close to impossible due to its randomness.
Outside
of dedicating a true sine wave to the boiler, what alternatives are out
there? Its been years since I explored line filters, but as I recall
they
were extremely inefficient and not all that cheap. Thanks.
Kirk Herander
Vermont Solar Engineering
802.863.1202
fax 802.863-7908
NABCEP(tm) Certified Solar PV Installer
Xantrex Certified Dealer Charter Member
NYSERDA-eligible installer
VT Solar Incentive Program Partner
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
EMAIL CONFIDENTIALITY NOTICE:
The preceding message (including attachments) is covered by the Electronic Communication
Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by
attorney-client or other privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you are hereby notified
that any retention, dissemination, distribution, or copying of this communication is
strictly prohibited. Please reply to the sender that you have received the message in
error, then delete it. Thank you.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list