The way I read this:

 - The sum of the breakers can never exceed 120 % of the rating of the buss.

 - If the sum of the breakers is less than or equal to the rating of the
panelboard ( 0 to 100%) the breaker may be positioned anywhere on the buss.

 - If the sum of the breakers is greater than the rating of the panelboard
(101 TO 120%), it must be positioned opposite the main and a label affixed.

MPF

-----Original Message-----
From: Darryl Thayer [mailto:daryl_solar at yahoo.com]
Sent: Tuesday, January 15, 2008 6:39 PM
To: re Wrenches
Subject: placment of inverter breaker [RE-wrenches]



HI all
new code 690.64 B7 does this mean that as long as I
have a breaker at the opposite end of the panel board,
I can have a breaker rated at the busbar rating?  Or
just that I must always place my inverter breaker at
the opposite end and the old 20% of busbar applies?
Thanks Darryl


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list