We may have missed threads on this subject, so I apologize in advance if the
information is out there already. If it is I would appreciate the starting
date of the thread(s) and I will track it down.

We have installed four Outback/GroSolar grid-tied battery backup systems,
and two more are various stages of design and bidding. They're relatively
straightforward to deign and install, but I do have some criticisms of their
"rating game" and the fact that the California Energy Commission power
rating and rebate for the 3,600 W (48V) system is surprisingly low. 

Here are my questions in no particular order of importance:

(1)   If the Outback system is based on "grid-tied loads" and "critical
loads" which are isolated from each other, do the Sunny Island AC2
(gen/grid) and AC1 (loads/SBs) serve the same purpose? With the SI system,
where exactly are the conventional (non-critical) loads connected? To AC2?
To the utility side of the Gen/Grid relay?

(2)   If the Outback system has a single set of PV modules and charge
controllers that provide the conditioned voltage on the 48 V buss, and the
Sunny Island system can have a hybrid mixture of conventional grid-tied
PV/inverters and PV/charge controllers - what additional capabilities are
there with the Sunny Island approach? Can the SI approach be configured more
inexpensively for the same functionality.

I have a couple of other questions, but these will suffice for now. Thanks
in advance for the help.

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com  

 


[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list