SMA Combi-Switch questions about UL rating [RE-wrenches]
Phil Undercuffler
p.undercuffler at conergy.us
Fri Dec 14 19:17:22 EST 2007
If SMA had just "packaged" the HU361RB with fuseholders, then yes the
11.5A (18/1.56) limitation would still apply. However, since SMA took
the extra step (and expense) to submit the product to a Nationally
Recognized Testing Lab (NRTL) and received a listing on it, then the new
specifications (40A max, 32A max continuous, 10a per pole) applies.
I believe the bottom line on the Combi-Switch is that SMA makes a
product designed to fill a certain niche, using an off the shelf
disconnect (the HU361RB) for the core. They, as the new manufacturer,
got that product Listed by a NRTL to a certain performance
specification. The Listing is held by SMA, and they (not SqD) are
responsible for it. As long as you install the Combi-Switch within the
limits of its design and according to the manual, it should be
acceptable.
And yes, you can use the HU361RB for more than 11.5 amps -- you just
wire it old school, with two poles in series (drawing B on the following
doc:
http://ecatalog.squared.com/techlib/docdetail.cfm?oid=09008926800f998d )
That will allow you to run 24A ISC through that switch to a single
inverter, as the non-fusible switches are rated at 100% continuous.
However, you can usually stuff more wattage through the switch by using
the recommended wiring for PV systems: 11.5A per pole x 3 poles = 34.5A
ISC total.
------------------------------------------------------------
Phil Undercuffler
Technical Services Manager
Conergy, Inc.
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Office | 505.473.3800 x4841
Fax | 505.473.3830
www.conergy.us
------------------------------------------------------------
-----Original Message-----
From: Larry Crutcher, Starlight Solar [mailto:larry at starlightsolar.com]
Sent: Friday, December 14, 2007 4:51 PM
To: RE-wrenches at topica.com
Subject: RE: SMA Combi-Switch questions about UL rating [RE-wrenches]
> Larry, the way I understand it Sq D makes this switch for SMA (both
> German companies). Why would they agree to do this if it can't be
used
> for anything? I mean if you can't put 4 strings on it what is it?
>
> It happens we have used it only with the Sharp 170 so far. Isc is 5.5
> so 2 strings on 1 pole is 11 amps. Its rated for 11.5 amps short
> circuit. Maximum current is 18 amps per pole. I think this is the
> intended use and also that Sq D and SMA make good products and have
good
>
> engineering. But I may be all wet. You know - like the time I thought
I
>
> was wrong but it turned out I was right after all?
That's the point of my question, why did (could) they do this? If the
switch was originally de-rated by Sq D to 11.5 amp per disconnect, not
per pole, to receive a UL listing, bla, bla...
If it will not cause arcing or be a fire hazard, that's a good thing.
Sorry for being anal-retentive here but it is still illogical to me.
Thanks for all the suggestions.
Larry Crutcher
Starlight Solar
Yuma, AZ
Renewable Energy Products Powered by STARLIGHT
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list