The code includes # 6:
200.6 Means of Identifying Grounded Conductors
(A) Sizes 6 AWG or Smaller
Ray
On Dec 10, 2007, at 11:14 AM, Mark Frye wrote:
>
> OK, Thanks Ray. I missed that. The call out is still smaller than #6,
> not #4, but your point is well taken and much appreciated.
>
> Interesting stuff. So as long as you use USE-2/RHW-2 or similar
> all the
> way thru from module to inverter, you can mark #6 or smaller, but
> if you
> transition to THHN or similar, in a box on the roof for instance,
> the #6
> or smaller has to be factory colored.
>
>
> R. Walters wrote:
>>
>>
>> RIght on the same page, man.
>> 200.6 (A) #2 allows PV system conductors #6 and smaller to be
>> taped.
>>
>>
>> Ray
>> On Dec 6, 2007, at 7:40 PM, Mark Frye wrote:
>>
>>>
>>> Ray, I am not sure where you are getting this?
>>>
>>> According to Article 200.6 (B) only wires #6 or larger can be
>>> identified
>>> "(3) At the time of installation, by a distinctive white or gray
>>> marking
>>> at its termination....."
>>>
>>> What am I missing?
>>>
>>>
>>> R. Walters wrote:
>>>>
>>>>
>>>> Code allows us
>>>> to tape PV wires smaller than #4.
>>>
>>>
>>> - - - -
>>> Hosted by Home Power magazine
>>>
>>> To send a message: RE-wrenches at topica.com
>>>
>>> Archive of previous messages: http://lists.topica.com/lists/RE-
>>> wrenches/read
>>>
>>> List rules & how to change your email address: www.mrsharkey.com/
>>> wrenches/etiquette.php
>>>
>>> Check out participant bios: www.mrsharkey.com/wrenches/
>>>
>>> Moderator: michael.welch at homepower.com
>>>
>>
>> R. Walters
>> Solarray.com
>> NABCEP # 04170442
>>
>>
>>
>>
>> --
>> [Non-text portions of this message have been removed]
>>
>
>
>
> Berkeley Solar Electric Systems
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
R. Walters
Solarray.com
NABCEP # 04170442
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list