Friends:
As you all know, the 2005 code allows for PV source conduit to enter a
building envelope without first passing through a disconnect IF the conduit
is metal. Does anyone have factual knowledge if this will change for 2008?
William Miller
At 04:34 AM 12/7/2007, you wrote:
>For what its worth - we have stopped running a DC conduit in the roof unless
>a DC disconnect is installed at the roof penetration as required by the 2008
>NEC. The reason for this new requirement (as far as I know) is to prevent
>firemen (firepersons?) from encountering live high voltage DC wires in the
>unfortunate occurrence that they have to open the roof. I miss that clean
>look of no conduit on the roof, but in this case we decided that safety
>comes first, not to mention it will eventually be code.
>
>
>Andrew Truitt
>Standard Solar Inc.
>NABCEP certified PV installer
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list