Thanks all for the help with this problem - Here are a few things I 
would check and try... 

1. Be sure that in the inverter's programming that the AUX OUTPUT is set 
to "REMOTE" or else you can get problems exactly like described...

What happens is that the inverter tells the AUX output to turn on for 
some other reason (say vent mode) then the AUX will come on until the 
MATE "sees" it on and tells the inverter to turn it off... because the 
AGS is enabled but the AGS thinks that the generator should be off - the 
resulting situation is exactly what you described - on for a few seconds 
then off - especially the part about it occurring when the AGS is set to 
off or manual.  I only recently found out that this happens this way 
myself... 

2. How big is the relay you are using to signal the generator? If its 
too large of a load then the inverter's AUX OUTPUT 12VDC power supply 
may cycle the relay on and off - sort of as described (although this 
doesn't answer why its happenning when the AGS is set to manual/off).

3. Some kind of problem with the generator - If the generator's AC 
output goes out of spec to the inverter the AGS system will signal the 
generator to stop - which will click the relay.  I would advise testing 
the generator with the two signal wires jumpered together and see what 
happens then.   

(I always put in a toggle switch to allow this to be done - as well as 
to block the gen start signal as well - just use a SPDT switch with the 
one of the gen start wires to the common and one of the switch contact 
to the AGS relay and the other switch contact to the other gen start 
signal wire - in one switch position the gen start relay signal goes 
through - in the other the generator is forced to run regardless of the 
AGS system.  If you use a "center off" type switch then you can also 
have a "disabled" position in the middle as well.)

Are you using a two-to-three wire adapter?  What is the model / brand of 
the generator?  How many kW is it rated at? 

I will think about this more tonight...

Christopher 


Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com  
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030  


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list