Outback island [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Mon Dec 3 13:18:56 EST 2007
Hey Darryl -
The best solution for questions like this is to detail everything you
know in an email and send it to myself or tech support and then we can
give you a detailed response.
Roy Dyngen is another resource here at OutBack on these larger / more
advanced applications.
There only real problem with doing a "tri-stack" configuration for
120/240 VAC - is that the X-240 will attempt to keep the loads 50/50 %
between the two legs. What you will probably see (due to the limit of
the X-240) is that it ends up being 60/40 % balance.
So - if the grid-tie inverter is 240VAC and 10kWAC then I would advise
going with a quad stack instead. If the grid-tie inverters are less say
8 kW total - then a tri-stack should be fine.
This also is a good situation for using the PSX-240 version rated at
6kWAC with its separate enclosure and built in fan.
Christopher
Darryl Thayer wrote:
> I have a customer with interest in an Outback Island system (AC coupled
> back up). I imagine I will have to get the right outback person on the
> phone, (first attempt tech did not understand questions)
> Has anyone done a 10 kW or three GVFX 3648 stacked into a Outback Island
> (AC coupled) configuration? If not I will try at my school to see what
> happens.
> What I am thinking is 2 inverters on one leg and the third on the other
> with the X240 coupling to balance the loads/feeds.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list