I think we are agreeing on most of this - other than one critical point:
On both the OutBack and Midnite AC bypass systems - the AC input or Gen
input breaker does not disconnect power from the bypass breaker - they
are not connected in series - each has there own connection to the AC
input bus inside the enclosure.
So turning off the AC input breaker does disconnect power to the
inverter. We agree here.
Switching the AC output breaker to the "OFF" position also disconnects
the inverter from the AC loads. We agree here too.
On the Midnite AC bypass system - turning off the AC output breaker for
the inverter forces the AC bypass breaker to the ON position. This is
the flaw and is what is not acceptable in my opinion.
If the generator was on when a problem occurred with an AC load -
turning the AC input breaker off results in the inverter still powering
the loads. Switching the AC output breaker OFF then turns the bypass to
the ON position - connecting the generator directly to the loads.
The only solution I see with this system is installing another breaker
into the system for shutting off the generator to the entire system.
With the OutBack AC bypass plate system - this is not required - you
simply switch all of the breakers to the off position and nothing is
energized.
Christopher
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list