Larry Crutcher, Starlight Solar wrote:
> Trojan batteries are some of our top sellers to RV'ers and they call for
> 2.47vpc absorb voltage. The MS2012 is fixed at 2.43vpc. Not too far off
> but it would be nice to have it adjustable.
2.43 VDC per cell is 14.58 VDC
2.47 VDC per cell is 14.82 VDC
The difference is 0.24 VDC (for a 12 VDC system)
This can be the difference between a wasted set of sulfated batteries
and a good healthy set of batteries.
I know many wrenches who who never accept these low of a absorption
voltage for a system - I think the batteries would never be fully
charged by a generator. I know many who routinely set the
bulk/absorption setpoint up in the 15 to 15.4 VDC level with non-sealed
batteries.
Christopher
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list