Jay - thanks for the clarification - but here is my issue for you - 

The AC input breaker only disconnects the power from the AC input of the 
inverter - the AC bypass still has AC power connected to it even when 
the AC input breaker is off.  

When the Midnite AC bypass is set to the bypass mode - the AC loads are 
then powered through the AC bypass breaker and there is no way to turn 
off the power to the AC load center.  

This doesn't seem acceptable to my understanding of the NEC.