Flex ware inverter bypass slide [RE-wrenches]
Jay Peltz, Peltz Power
jay at asis.com
Thu Nov 29 20:10:31 EST 2007
<x-flowed>
Ah no Christopher,
He is talking about the AC input breaker next to the inverter bypass
switch.
I was talking about the smoothness of the bypass switch, nothing more.
jay
peltz power
On Nov 29, 2007, at 5:02 PM, Christopher Freitas --- OutBack Power
wrote:
>
> So you are saying that its OK that the operator has to walk all the
> way
> out to where the generator is to shut off its circuit breaker in order
> to disconnect all sources of power from the loads?
>
> And you think this is acceptable and code compliant? Come on now...
>
> Christopher
>
>
> Todd Cory wrote:
>>
>> With the generator input breaker off, switching to bypass shuts
>> everything off since you are bypassing to a de-energized circuit.
>>
>> Todd
>>
>>
>> Christopher Freitas --- OutBack Power wrote:
>>
>>> jay peltz wrote:
>>>
>>>
>>>
>>>> Whats funny is that Midnite solars box's work perfectly,
>>>>
>>>>
>>>
>>> Perfectly Huh? I strongly disagree - the Midnite AC bypass is
>>> not safe
>>> or compliant with the UL standards for a System Bypass or the NEC
>>> code
>>> because:
>>>
>>> The AC bypass bypass slider plate does not allow you to set both
>>> circuit
>>>
>>> breakers to the OFF position.
>>>
>>> It also does not allow the handle of the circuit breaker to indicate
>>> that it has tripped due to the extremely small opening for the
>>> handle in
>>>
>>> the AC bypass slider plate.
>>>
>>> The AC bypass slider plate also covers up the labeling on the
>>> breaker as
>>>
>>> to the amperage and on/ off status.
>>>
>>> I think these are serious safety issues with the Midnite product.
>>>
>>> Christopher Freitas
>>> OutBack Power Systems, Inc.
>>> cfreitas @ outbackpower.com
>>> www.outbackpower.com
>>> Arlington WA USA
>>> Tel 360 435 6030
>>>
>>
>
>
>
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas @ outbackpower.com
> www.outbackpower.com
> Arlington WA USA
> Tel 360 435 6030
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list