>From the 2005 NEC Code Handbook page 1021: Ground-fault detection and 
interruption for PV systems should not be confused with the requirements for 
GFCI protection, as defined in Article 100. A GFCI is intended for the 
protection of personnel in single-phase ac systems. It functions to open the 
ungrounded conductor when a 5-mA fault current is detected. In contrast, 
devices meeting 690.5 are intended to prevent fires in dc PV circuits due to 
ground faults.

I haven't kept up with SDHW system developments, but what's wrong with using 
an in-line, fast-blow fuse on the low-wattage PV module circuit?

----- Original Message ----- 
From: "Mark Frye" <markf at berkeleysolar.com>
To: <RE-wrenches at topica.com>
Sent: Friday, November 16, 2007 10:34 AM
Subject: RE: GFP on SDHW pv pump? [RE-wrenches]


>
> The PV module on the solar fan is most likely an integral part of the
> larger UL listed device.  This would create a listed appliance which is
> not the purview of the inspector.
>
> If the solar panels for the water pumps were part of a complete package
> which is UL listed, it may side step this problem.
>
> But the real problem is uninformed, unreasonable inspectors overstepping
> the bounds of their discretion.
>
> MPF
>
> jay peltz wrote:
>>
>> What comes to mind are solar fans.  ( fan and panel in one unit.
>>
>> So mount the panel on a box with pump inside, mount on the roof near
>> the panels call it good.
>>
>> jay
>>
>> peltz power
>>
>> Don't even get me started about JW
>>
>> j
>>
>
>
>
> Berkeley Solar Electric Systems


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list