Xantrex XW [RE-wrenches]

Mark Edmunds mark.edmunds at xantrex.com
Wed Nov 7 13:40:59 EST 2007


Hi Dan - 

In a system with an existing neg-ground bond the charge controller's
internal ground fault fuse is not required, and should be removed to
make the grounding scheme clear. If you do need the PV ground fault
protection the external system bond will need to be removed to allow the
internal protection circuit to work.

We will be posting a note on our download site in a day or two to help
clarify this whole issue...somehow this missed getting in the first
release of the manual!

Thanks

Mark



Mark Edmunds
Xantrex Technology Inc.

-----Original Message-----
From: Dan Rice [mailto:danrice at scinternet.net] 
Sent: Wednesday, November 07, 2007 7:03 AM
To: RE-wrenches at topica.com
Subject: Re: Xantrex XW [RE-wrenches]


Mark,

Please clarify the point about using the XW controller on a system with
an existing negative-ground bond. Do I understand correctly, that the
controller requires the 1A fuse be installed to operate, even if there's
an external bonding conductor? If so, and there's already an existing
negative-ground bond in the system, this amounts to having two "bonding"
points, which is prohibited by NEC. Besides the fact that, with parallel
current paths, the fuse may blow because current may be flowing through
it (it's become a parallel conductor in the negative conductor current
path).
Please clarify.

Dan Rice
Abundant Sun, LLC.


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list